First, see where each code, standard, etc. applies. In my opinion, busbar was almost right when recommended the IEEE standards. But there are some other aspects you should take into consideration.
As far as I know, the reason for the NEC is not so specific about the generation facilities is that this code does not apply to this type of facility. Power generation and transmission facilities are owned and operated by companies that have developed their own standards, guidelines, rules, etc. If you work with such a company, you should see what is the general accepted practice over there. If you work with someone else, try to find out the norms, guidelines, etc. of the local power generation company or other applicable local codes. Do not forget about the standards, policies, recommendations, etc. of the regional reliability organization the local company is part of.
Here is an example. Before 1998, in the Canadian province of Ontario it was only one power generation, transmission and distribution company, Ontario Hydro. In 1998, the local government decided to create an electricity market and OH was divided into 3 major types of companies: power generation, transmission and local distributors. All are now among the market participants and should comply with the Ontario codes and market rules. One of these codes is the Transmission System Code, which governs both generation and transmission sectors. This code was issued by the Ontario Energy Board (
appointed by the local government and is based not only on the experience of the former OH, but also takes into consideration the requirements of NPCC (North-East Power Coordination Council,
and NERC (North American Electric Reliability Council,
where the Ontario power systems are part of.
As guidance for what you need, here is what the abovementioned code states in Appendix 1, Schedule G-Technical Requirements for Generators, 1.1.1 (
, page 78 of the pdf file): ‘A high voltage interrupting device (HVI) shall provide a point of isolation for the Generator’s station from the transmission system. (...) The HVI shall be a circuit breaker unless the Transmitter authorizes another device.’ So, here, there is no doubt about the mandatory use of a CB on the HV side.
Immediately after this, at 1.2 Typical Generator Protection, it is stated: ‘The typical technical requirements for Generator protection SHOULD BE followed, ‘[my emphasizing, vic3fan] ‘as set out in Exhibit F.1 of Schedule F and Exhibits G.1 and G.2 of this Schedule G’. Well, in these G.1 (page 81) and G.2 (page 82) a circuit breaker is also used between generator and transformer. Again, there is no doubt about the necessity to comply with this rule.
As you can see, for an Electrical Designer whose job is to devise a generation facility in Ontario, the things are very clear. See your local requirements. Also, keep in mind that the designer might be responsible for further incidents during the operation of that part of the power system, so it's better to anticipate some potential troubles and to not give the cost reduction the first priority.