The use of a generator is probably your best bet. You'd need a big one to handle the 10,000A, say a 3750kVA transformer with a 208V secondary, and a 12kV (anything from 10 - 15kV) primary. Then, feed that primary with a 480V generator. If the transformer had a 12470V primary, the primary current would need to be 1/60 of your 10,000A or 167A. The secondary, the 208V side, would be essentially short circuited, and you would control the generator output to produce the voltage necessary to drive 167A into the primary of the transformer. All will be well, the transformer will be vastly over rated voltage wise, but running right at its ratings current wise, the generator will not need to exceed 480V to produce the 167A. In theory you might be able to get that out of a 150kW generator, but because that short circuit will be essentially all reactive, you may need to go to a 250kW or even 300kW generator to keep the reactive current within the generator capability curve. Then again, it may take a 500 or 750kW generator just to energize that 3750kVA transformer. If you could put a 10,000A breaker on the secondary of the transformer, you could have the transformer connected to the generator as the generator voltage builds and then not have any inrush. You'll get your current on the 208V side of the transformer, but no voltage to speak of; but 10,000A is nothing to be trifled with, even at close to zero volts.