Many Combustion Turbines(CT's) have generators that seem to be rated much higher than the turbine maximum output. Turbine output can vary 20-30% with ambient temperature changes, with higher output at lower temperatures. The CT nameplate may indicate the reduced turbine output at the specified high ambient conditions, while the generator nameplate lsits its capability at standrd temperatures.
Gas turbines are usually designed as package units with a standard size generator to match the standard turbine package. It is not economical to have a seperate generator design for every application of a standard product, especially when all of the type testing and other Quality Control issues are considered. One design covers the complete range of output for the turbine package, so it will seem to be oversized in some cases.
The generator nameplate is specifed at some ambient temperature and cooling water or cooling air temperature, or H2 pressure and temperature. Most of the time, this does not match the ISO temperatures used in the turbine rating. When you adjust the turbine output and generator capability curves to the same amvient conditiosn, teh discrepancy is not as large.
Adding inlet air cooling equipment or using water injection can boost gas turbine output significantly. In some cases the generator is sized to allow future turbine output enhancements.
Remember that turbines are rated in MW, generators in MVA. Soem bids for Saudi Arabia required lower than normal power factor (0.80 lagging)capabililty with a margin. This led to oversize generator requirements.