When designing a monoslope roof building for wind hitting the sidewalls of the building (parallel with the roof slope) I'm curious how some of you would do this and so I have several questions. The building I am referring to would have the high side completely open and the low side closed with a agricultural roll-up fabric curtain. Height on the high-side is 22' and on the low side perhaps 14'. The roof width is 60'
1. When analyzing the MWFRS loads on enclosed buildings, the internal pressure components cancel out. On a building as "open" as this, I assume that is NOT the case.
2. With the low side curtain wall being the windward wall, using the middle elevation of Fig 6-6 in ASCE 7-05 I would apply windward forces to the low wall AND internal suction forces to the same wall and nothing on the high side as is there is no surface to apply load to. Of course I would apply forces to the roof as well. I'm comfortable with this.........unless somebody disagrees.
3. My biggest question then is how I analyze wind coming from the high side. Like a venturi, wind is funneled towards the low side wall. (See the right elevation of the mono-slope building in Fig 6-6 without a windward surface to take loads at the high side) I know I need to apply leeward forces to the outside of the low wall as is shown in addition to the forces on the roof. In addition to that, do I apply windward pressures to the inside of the low wall using a Cp of .8? Do I add to that the Cpi of .55 to the .8? Would I just use an internal pressure only with a Cpi of .55? I'm unsure what is right here.
4. Lastly.........a fabric curtain as a wall. Is it commonplace to determine what the allowable wind loading is on the curtain and at pressures above that, assume that the curtain "takes flight" and now the internal pressures drop as there is no longer a low-side wall to take lateral wind pressure?
Thanks for your thoughts!!
1. When analyzing the MWFRS loads on enclosed buildings, the internal pressure components cancel out. On a building as "open" as this, I assume that is NOT the case.
2. With the low side curtain wall being the windward wall, using the middle elevation of Fig 6-6 in ASCE 7-05 I would apply windward forces to the low wall AND internal suction forces to the same wall and nothing on the high side as is there is no surface to apply load to. Of course I would apply forces to the roof as well. I'm comfortable with this.........unless somebody disagrees.
3. My biggest question then is how I analyze wind coming from the high side. Like a venturi, wind is funneled towards the low side wall. (See the right elevation of the mono-slope building in Fig 6-6 without a windward surface to take loads at the high side) I know I need to apply leeward forces to the outside of the low wall as is shown in addition to the forces on the roof. In addition to that, do I apply windward pressures to the inside of the low wall using a Cp of .8? Do I add to that the Cpi of .55 to the .8? Would I just use an internal pressure only with a Cpi of .55? I'm unsure what is right here.
4. Lastly.........a fabric curtain as a wall. Is it commonplace to determine what the allowable wind loading is on the curtain and at pressures above that, assume that the curtain "takes flight" and now the internal pressures drop as there is no longer a low-side wall to take lateral wind pressure?
Thanks for your thoughts!!