The reactive power was discussed in thread238-138258. But how to control the reactive power at the generating end? The answer is given in
, for example, with figures and several equations.
The generator is a voltage source, when it is considered as an electrical component in a network. The parameters of a voltage source, or, in this case, a generator in a large ("infinite") network are the magnitude and the phase of the internal voltage. This internal voltage is induced in the stator windings by the rotating magnetic field of the rotor. The voltage source, i.e. the generator has also an internal impedance. The induced voltage can be thought to be behind this fixed internal impedance.
A generator has several variables that one wants to control: The magnitude and phase angle of the internal voltage, the power, and the reactive power, at least. There are two control variables: the throttle position of the prime mover and the magnetisation current. How do you control those four variables with these two control variables? Well, you don't, at least not at the same time.
The effects of the throttle and the magnetisation current are not quite simple. When one opens the throttle a little from the present position, the generator attempts to increase the rotating speed, i.e. the frequency. But if the generator is a part of a large network containing several generators, it cannot increase the speed, because it has not enough power to force all the other generators to accept the same speed. The result is that the relative position of the rotor only advances a little. This means that the phase angle (the "power angle") of the induced voltage changes in the positive direction, because it is determined by the relative rotor position.
When the magnetisation current is increased, the magnet of the rotor becomes stronger and the magnitude of the induced voltage in the stator windings increases. But a larger voltage means a larger current and a larger power and a larger loading of the prime mover. This loading attempts to slow down the prime mover and the rotor. Again, it is not possible to reduce the rotating speed because of the large network. If the throttle position and thus power are kept constant, the relative position of the rotor retards a little, so that the "power angle" becomes smaller.
In a summary: The magnetisation current controls both the magnitude and phase of the internal voltage. The throttle position controls the phase of the internal voltage. These controls must be used together in practice, as rcwilson writes.
The change in the power and the reactive power depends on how these two control variables are operated. The analysis is fortunately simplified by the assumption that the generator sits in a large network containing several generators. This means that the voltage at the terminals of the generator can be assumed to be constant. The reason is the same as that for the constant frequency: One generator cannot do much about the voltage at the terminals, it can only adjust the internal voltage.
The internal impedance Zs of a generator is typically almost purely inductive, the resistance is very small, Zs = jXs. If Ef is the induced internal voltage, and V is the voltage at the terminals, then the generator current is simply Is = (Ef – V)/jXs = -j(Ef – V)/Xs. This current is 90 degrees behind the voltage difference Ef – V, but it may lead or lag the voltage V at the terminals.
It is known that 1) the voltage V is given, 2) the reactance Xs is given and fixed, 3) the magnitude and phase of the voltage Ef are controlled by the magnetisation current, and 4) the phase of Ef is controlled by the throttle position. It should now be possible (but not necessarily easy) to see what happens to the real and reactive power in different control operations. (Remember, the complex power P + jQ = voltage times the complex conjugate of current.)
So, what happens, when the power is increased, but the magnetisation current is kept constant, as rmw asks? See figure 2.6b in the above reference. The induced voltage vector Ef turns counter-clockwise, with a constant magnitudes, i.e. the phase moves in the positive direction. As a consequence, the phase of the current moves also in the positive direction and its magnitude increases. The reactive power Q becomes less negative first, then zero, and eventually positive. See figure 2.8 in the link above for the opposite case of a constant power and varying magnetisation current.
That was a lengthy explanation, and I hope that I got it right.