I would check your data base to determine the percentage of full load current is used for the fuses for smaller motors. You may also check the time current characteristics and attempt to match that also. Also check your codes for the acceptable range of fuses.
If these motors are larger than your data base, and in the medium voltage group, the fuses are for short circuit protection of the conductors feeding the motors.
Protection of the motors will be by overload relays, and possibly by thermal modelling, differential protection and temperature monitoring.
If, despite the motor protection, the motor burns up, or if there is physical damage to the motor circuit conductors the fuses will interupt the fault current.
respectfully