To further complicate things, IEEEC57.13 (CT and VT standard) does not require CT secondary windings to be equally distributed. Which means that many times the accuracy/saturation performance is not linear. For example, if you buy a 1200:5A MR C800 rated CT, if the performance was linear, you could expect a C400 rating at 600:5A. However, if the windings are not equally distributed, the performance at 600:5A tap may be worse/lower than C400.
Most of the time, the lower ratios are used to match up to other CTs for differential protection. Of course, most of the 'C' ratings for modern substation applications are over-kill for newer electronic relays, which bails many a protection engineer out of mis-applications.
Advice to users from a vendor of IT's, always specify that your multi-ratio CT windings are equally distributed.
You would be surprised at how many people think you can apply the full-winding performance to any tap arrangement and get the same performance. Some even try to use them for revenue meterings.