Hi,
I have an existing 7UT86 protection that measueres on one CT on the primary side of a three-winding 130/6.6 kV Transformer and includes the cable all the way up to the feeding switchgear (roughly 1 km) for differential protection. The feeding switchgear was before an ABC-switchgear but will be changed to a double-breaker scheme. This means I need two CTs on the primary side in order to cover the same zone as before. Could I put the two CTs on the double breaker switchgear in parallel so that I don´t need to change so much and get roughly the same protection zone as before? The reason is that I preferably don´t want to perform work at the site where the 7UT86 is placed.
Regards
M
I have an existing 7UT86 protection that measueres on one CT on the primary side of a three-winding 130/6.6 kV Transformer and includes the cable all the way up to the feeding switchgear (roughly 1 km) for differential protection. The feeding switchgear was before an ABC-switchgear but will be changed to a double-breaker scheme. This means I need two CTs on the primary side in order to cover the same zone as before. Could I put the two CTs on the double breaker switchgear in parallel so that I don´t need to change so much and get roughly the same protection zone as before? The reason is that I preferably don´t want to perform work at the site where the 7UT86 is placed.