genhead
Electrical
- Jul 26, 2001
- 73
A client has a temporary installation of 4 x 600kw 400v generators connected to a 400/11,000v 3MVA step-up transformer.
The generators are self-contained mobile units, each with its own circuit breaker. Each generator is cabled from the load-side of its circuit breaker to the LV terminals of the transformer, making the LV transformer terminals a common bus. There is no other 400v load, and the 11,000v feeds into an MV switchboard.
The client has been advised by somebody that additional circuit breakers must be installed at the load-end (transformer-end) of each set of generator cables, but his advisor was unable to provide any reasons why, other than "it is bad industry practice".
Can anybody please confirm if these circuit breakers are required, and why/why not.
The generators are self-contained mobile units, each with its own circuit breaker. Each generator is cabled from the load-side of its circuit breaker to the LV terminals of the transformer, making the LV transformer terminals a common bus. There is no other 400v load, and the 11,000v feeds into an MV switchboard.
The client has been advised by somebody that additional circuit breakers must be installed at the load-end (transformer-end) of each set of generator cables, but his advisor was unable to provide any reasons why, other than "it is bad industry practice".
Can anybody please confirm if these circuit breakers are required, and why/why not.