The bigger the better. Running towers in parallel will prevent problems with shrink and swell with starting and stopping of condenser water pumps. Keep velocity below 3 fps, max conditions. It's not like piping that gets distributed throughout a building; you might be talking about a 30' run. Go for the 14" vs. the 10" (as an example) to avoid problems.