tin2779
Electrical
- May 26, 2007
- 38
Hi...
I am looking for a explanation in regards to this obsolte product P4 A relay from Multilin.
A 225 a breaker is feeding two 100 HP fans with independent soft starters. The application is ventilation fans.
The pitch of the fans has been changed, so they are not taking full 90 A as they should have been on 600 V.
The steady state current for both fans is 65 and 72 A respectively. Both fans have 30 KVAR cap banks which come online when the motor comes to speed and the soft starting circuit is out of the picture.
The fans are started after certain interval of each other.
After Fan#1 goes up to speed and the capacitor comes online, the main breaker trips.
I tried to find explanation with Multilin but not much help.
It looks like this relay has a single phase detection element that can be disable.This element works on based on non sinusoidal voltage and current unbalance.
Any suggestions, why this is happening. When they disconnect the capacitors everything works fine.
Thanks
I am looking for a explanation in regards to this obsolte product P4 A relay from Multilin.
A 225 a breaker is feeding two 100 HP fans with independent soft starters. The application is ventilation fans.
The pitch of the fans has been changed, so they are not taking full 90 A as they should have been on 600 V.
The steady state current for both fans is 65 and 72 A respectively. Both fans have 30 KVAR cap banks which come online when the motor comes to speed and the soft starting circuit is out of the picture.
The fans are started after certain interval of each other.
After Fan#1 goes up to speed and the capacitor comes online, the main breaker trips.
I tried to find explanation with Multilin but not much help.
It looks like this relay has a single phase detection element that can be disable.This element works on based on non sinusoidal voltage and current unbalance.
Any suggestions, why this is happening. When they disconnect the capacitors everything works fine.
Thanks