Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations The Obturator on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Multicore screened cables

Status
Not open for further replies.

mhoult

Industrial
Sep 27, 2007
2
Can anyone advise me if earthing a spare conductor in a multicore cable will casue me any concerns? The device is a PT having a 4-20mA signal. The screen is isolated at the device end.

Many thanks
 
Replies continue below

Recommended for you

In my experience you're doing the exact right thing. Earthed spares and shield at the controller end of the cable, insulated ends at the device.
 
What Keith said;- One end only.
respecfully
 
I should have been a little more precise. What I want to do is remove the need for external earthing and use a triple with one of the cores being the bonding conductor. The screen/armour is on earthed at the control end, the device is also connected to pipework (which is earthed) and sometime a bracket (that is connected to the main skid). Lookind at all the EMC and bonding IEC's I cannot find anything that prevents this, although a BP specification states that usually both ends of a 'spare' core will not be earthed at each end. Shell and total are prety similar.

Your help is once again appreciated.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor