COEngr
Structural
- Sep 17, 2013
- 3
All,
My firm is getting into the delightful realm of multi-story wood construction and we are trying to get an understanding for how to accurately calculate drift in the wall so we can demonstrate compliance with ASCE 7-10 12.12. Most examples I've seen only address single story structures. We initially relied on an example published by WoodWorks for a 5-over-1 podium. There seem to be two fundamental issues with this example that we would love some guidance on.
1) When calculating the deflection of a multi-story wood shearwall, do you treat it as a single cantilevered wall with forces delivered at each level (as you would a masonry or concrete shearwall with flexible diaphragms)? Or do you consider the wall as (5) stacked cantilevered walls "fixed" at each levels and only as tall as the story (say 10ft)? The example seems to take the second approach but this doesn't not seem to be justified by statics.
2) When considering the elongation of the tension-rod anchorage system (rod, device, shrinkage residual, and crushing of the bearing plate/compression chords) to include in shearwall deflection calculations, do you sum the elongations up the height of building or only consider the elongation between stories? Keep in mind, the code specifies story level drift limits, not absolute deflection limits. The example seems to sum the elongations for systems without shrinkage devices but then doesn't sum them when shrinkage compensating devices are used (Tables 16/16A). How is this justifiable?
Any insight you can provide would be greatly appreciated!
My firm is getting into the delightful realm of multi-story wood construction and we are trying to get an understanding for how to accurately calculate drift in the wall so we can demonstrate compliance with ASCE 7-10 12.12. Most examples I've seen only address single story structures. We initially relied on an example published by WoodWorks for a 5-over-1 podium. There seem to be two fundamental issues with this example that we would love some guidance on.
1) When calculating the deflection of a multi-story wood shearwall, do you treat it as a single cantilevered wall with forces delivered at each level (as you would a masonry or concrete shearwall with flexible diaphragms)? Or do you consider the wall as (5) stacked cantilevered walls "fixed" at each levels and only as tall as the story (say 10ft)? The example seems to take the second approach but this doesn't not seem to be justified by statics.
2) When considering the elongation of the tension-rod anchorage system (rod, device, shrinkage residual, and crushing of the bearing plate/compression chords) to include in shearwall deflection calculations, do you sum the elongations up the height of building or only consider the elongation between stories? Keep in mind, the code specifies story level drift limits, not absolute deflection limits. The example seems to sum the elongations for systems without shrinkage devices but then doesn't sum them when shrinkage compensating devices are used (Tables 16/16A). How is this justifiable?
Any insight you can provide would be greatly appreciated!