MSJC (ACI 530) question on veneer

Status
Not open for further replies.

JAE

Structural
Jun 27, 2000
15,687
Section 6.2.2.10 in the MSJC (ACI 530) has a requirement that has changed a bit over recent editions.

In the 530-02
For seismic design category D, this code required masonry anchored veneer to be supported at each level independently at each level. (i.e. relief angles).

In the 530-05
For SDC D, this requirement was moved to ONLY apply to SDC E and F. No longer required for SDC D.

My question is - for the 530-08, has this remained the same? Is the requirement still only applicable to SDC E and F?

We are designing a project under 02, but was curious as to how this provision has developed over recent editions.

 
Replies continue below

Recommended for you

JAE,

I believe it is the same requirement. I am looking at ACI 530-08 section 6.2.2.10 and I read it the same... and there are no black lines indicating a code change for this section.
 