Right Tinfoil, I agree with your last obversation. The voltage drop (flicker) is the same for the unloaded and loaded condition of the supply transformer.
For the rest of you guys who said more information is needed to answer the question, you need to step back and see the big picture. This is a before and after calculation where only one variable is changed. The question does not ask for actual values, it just asks how changing one variable (transformer load current) affects another variable (dV/dt for starting a given motor). Sure, you can run a bunch of calcs and prove that there is a 2% difference between the two conditions because of some secondary effect or other, but nobody cares about that in the real world. Don't make the problem harder than it is.
And DanDel, a transformer is manufactured to provide the rated voltage at the rated kVA. I suggest you check with your local Sauare D engineering specialist. I did.
The application that led to this question is a mid-size condo that is experiencing (alledgedly) lamp flicker whenever the elevator starts. The elevator, which is a hydraulic unit, is fed from the main service transformer. Because I was brought in as an expert witness after everybody (including the serving utility) got lawyered up, I haven't been allowed access onto the property to physically observe and measure the actual installation. So I'm left to deal with theoretical 'what-ifs' at this point, hence the question.
Ironically, there is a condo a block away, with a smaller service transformer and a larger elevator motor that doesn't have lamp flicker. Ironic, because I am the design engineer of record on that condo!
Frank Starr, P.E.