We are testing VFD fed AC induction motor designed to MG-1, Part 31 for dynamometer application .The name plate ratings (at base speed 6000 RPM): 260 kW power, 450V, 436 FLA. This motor was loaded using eddy-current dynamometer at the rated torque of 413 Nm (measured by the load cell). The actual motor current measured and displayed by VFD (at rated torque) was around 500A. Motor vendor people witnessed the test and suggested that they re-rate the motor current to higher value. The power interface to the motor was designed based on current name plate value of 436A. When we blamed the motor vendor that motor re-rating would cause us significant re-work of infrastructure, their response was:
"Please note that NEMA allows the actual motor amps to deviate from the name plate amps by 10% when operated at rated voltage, power and speed".
Please advise what standard allows for that (if the above statement is true). Motor cable selection was based on name plate data, and we not recall any requirement to count for additional 10%.