Hello all,
Do you have any experience of running low speed (365rpm, 16 pole) motors with low power factor (0.56 @ 100% load, to 0.38 @ 50% load) on a VSD. In this instance the motor is 25kW with rated current of 80Amp. The VSD has been sized to the motor rated current not the motor kW, hence it a 45kW VSD. The motor in question is on a propeller pump and the mechanical engineer is certain that the hydraulic conditions are within the pump specifications but we get no flow, so naturally they suspect that the VSD is some how not spinning the pump at 50Hz. They also do not believe the current reading from the VSD which confirms that it is drawing full load current. Is there any chance that the poor power factor is upsetting the operation of the VSD?
Cheers Niallnz
Do you have any experience of running low speed (365rpm, 16 pole) motors with low power factor (0.56 @ 100% load, to 0.38 @ 50% load) on a VSD. In this instance the motor is 25kW with rated current of 80Amp. The VSD has been sized to the motor rated current not the motor kW, hence it a 45kW VSD. The motor in question is on a propeller pump and the mechanical engineer is certain that the hydraulic conditions are within the pump specifications but we get no flow, so naturally they suspect that the VSD is some how not spinning the pump at 50Hz. They also do not believe the current reading from the VSD which confirms that it is drawing full load current. Is there any chance that the poor power factor is upsetting the operation of the VSD?