EP007
Electrical
- Apr 1, 2008
- 47
Our team is discussing the need for motor differential protection on a 3000 HP motor, 4.16 kV. There is high resistance grounding, 10 A, which is important since a stator ground fault, is low current, and can be cleared quickly by the MPR (motor protection relay), without any time advantage of differential protection. Likewise, high level or solid 3L, LL faults and unbalance can be cleared quickly.
What we are left with appears to be low current LL stator winding fault, with a high impedance in the fault circuit, if that is possible. Does this sound correct?
What we are left with appears to be low current LL stator winding fault, with a high impedance in the fault circuit, if that is possible. Does this sound correct?