what if a 60 cycle motor use where the country provide a 50 cycle.what will wrong with the motor.
 
Do a search, this type of question was asked several times in the past.

See:
thread237-103432
thread237-100200
thread237-93389

etc.

Ralph

 
If the motor is designed for 60Hz operation and the conected to a 50Hz mains it will operate at 20% harder and it could burn the motor out. To prevent this you could put a transformer before it and decrease input voltage by 20%. If this is done the speed of the motor will be altered. Most of motors these days are 50/60Hz so you can use them on either mains.
 