I think the problem may be one of semantics. "Interrupt ratings" are for circuit protective devices and has to do with the devioce's ability to safely stop the flow of fault current. The magnetic trip setting of an MCCB has nothing to do with the fault current capabilities of the MCCB, they are related to the point at which the breaker will try to start opening the circuit. The interrupt rating has to do with the point at which the MCCB begins to emit shrapnel or fails to interrupt the fault.
But contactors are not used as interrupt devices*, so they will not show an "interrupt rating". A contactor would have a "breaking capacity" and a "Short Circuit Current Rating" (SCCR) which also used to be referred to as a "Withstand rating". As far as I know, only the breaking capacity might have anything to do with the magnetic current trip settings of a circuit breaker. In other words, the trip point of the breaker being that high means that the contactor may end up being asked to open under conditions up to that setting and the breaking capacity is where that would come in. But the breaking capacity of a NEMA contactor is several times the continuous current rating (I am without my copy of NEMA ICS-2 right now to look it up, maybe someone else has it).
From a fault current standpoint, the SCCR rating is the important issue. The contactor must also be able to avoid becoming shrapnel while it waits for the circuit protective device to clear the fault. But the SCCR rating can be done as part of a "series rating" by the manufacturer, because they can consider the "let-through" energy of the protective device as the maximum the contactor will see. So for instance, you may see that a contactor has an SCCR rating as a stand-alone device at only 5kA or 10kA, but if used in a tested and listed combination with a specific circuit breaker, the combination may be rated by the mfr as 65kA.
*The only time I see contactors have interrupt ratings are on vacuum contactors, because they are often used with protective relays in the same manner as a circuit breaker. Hence dpc's observation above.
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> faq731-376