RAgrawal,
Does your rotor have slip ring connections?
If you can monitor V & A imput to your main field winding, you can derive R in ohms
From there, and with the aid of your manufacturers cold resistance figures and ambient temperature taken at that time, you can use:
temp(Deg k)=[(R hot-R Cold/ R cold)x(234.5 + ambient)]+/- ambient difference (between hot and cold ambient)if the hot ambient is larger than the cold ambient, subtract the difference, if small, add the difference.
This should give you a figure accurate to say + / - 1 degree for average temperature, but will not give you information on 'hot spot' temperatures, or differences between trailing & leading edge temperatures and outhangs.
For that you need embedded PT100 RTD's or similar.