I've been involved in trouble shooting/critiquing the design of the AHU's at a large new hospital in the midwest where the engineer used a blow-through fan with the chilled water cooling coils and final HEPA filters downstream of the fan. The units were field erected and poorly constructed so there's a lot of bypass of the warm moist mixed air around the coils and through the gaps between the vertically stacked coils. I did not observe moisture carry-over off the fins but the final HEPA filters are loaded with water to the point they had to remove several filters to get some airflow. I suspect the moisture in the by-pass air has condensed on the cold filters. Most of it appears to have condensed on the underside of the cold intermediate drain pans. I talked to some friends at HVAC equipment manufacturers and they dug up an old internal memo where one of their engineers hypothesized that the pressure drop in the final filters caused cooling of the nearly saturated discharge air coming off the coils(50.0F DB/49.9F WB)and is the cause of the water on the filters. He cited Boyles Law(pV=MRT)and if P2 is lower than P1, it stands that T2 is lower than T1. I've never heard of this being a problem but also rarely use blow-through. With draw-through, the fan heat ends up increasing the spread between leaving dry bulb and wet bulb. The equipment mfgr. engineer said you could expect a 0.5F drop for each 1 in.w.c. drop. Anyone ever experienced this problem?