Saturated machine reactance use:
1.2.15 direct axis substranient reactance: X”dv - (saturated, rated voltage) is the apparent reactance of the
stator winding at the instant short-circuit occurs with the machine at rated voltage, no load. This reactance
determines the current flow during the first few cycles after short-circuit.
1.2.18 direct axis transient reactance: X'dv - (saturated, rated voltage) is the apparent reactance of the
stator winding several cycles after initiation of the fault with the machine at rated voltage, no load. The
time period for which the reactance may be considered X'dv can be up to a half (1/2) second or longer,
depending upon the design of the machine and is determined by the machine direct-axis transient time
Unsaturated machine reactance use:
1.2.16 direct axis subtransient reactance: X”di - (unsaturated, rated current) is the reactance which is
determined from the ratio of an initial reduced voltage open circuit condition and the currents from a threephase fault at the machine terminals at rated frequency. The initial open circuit voltage is adjusted so that rated current is obtained. The impedance is determined from the currents during the first few cycles.
1.2.17 direct axis transient reactance: X'di - (unsaturated, rated current) is the reactance which is determined from the ratio of an initial reduced voltage open circuit condition and the currents from a threephase fault at the machine terminals at rated frequency. The initial open circuit voltage is adjusted so that rated current is obtained. The initial high decrement currents during the first few cycles are neglected.