Hey all. I am working on a problem right now for a local contractor who incorrectly poured a foundation. The design called for a 5 foot deep frost wall with the finished floor grade and exterior grade at the top of the foundation. However, due to the presence of bedrock, the foundation was raised such that the floor is now 4.5 feet below the top of the wall sitting directly on top of the footing and the finished grade is still at the top of the foundation. The structure being placed on the foundation is an open garage type building with no interior walls to resist earth and wind forces.
My question is, how do you appropriately model this situation? I understand that modeling it like a retaining wall would be an option, however I'm not sure how to account for the strength at the corners of the wall where the other frost walls attach. Right now my largest concern is overturning. Currently I have about 850 ft-lb/ft of resisting moment while my overturing moment is more like 3250 ft-lb/ft. One thought I had was installing deadman anchors along the lenght of the wall, but I am not sure how to quanitfy the amount needed. Any help would be greatly appreciated.
My question is, how do you appropriately model this situation? I understand that modeling it like a retaining wall would be an option, however I'm not sure how to account for the strength at the corners of the wall where the other frost walls attach. Right now my largest concern is overturning. Currently I have about 850 ft-lb/ft of resisting moment while my overturing moment is more like 3250 ft-lb/ft. One thought I had was installing deadman anchors along the lenght of the wall, but I am not sure how to quanitfy the amount needed. Any help would be greatly appreciated.