OP said:
During the operation (prior to the failure), even on attaining full load current of >630amps, MW was not shooting up. Could this impedance have played a part for it? The transformers are all idential of 4MVA each, 11kV/185volts, with 18taps of equal voltage regulations.
Unequal transformer temperatures in similar transformers are an indication of circulating currents. Given similar transformers, the current will be greatest in the transformer with the highest effective applied voltage. (The term "effective applied voltage" is a simplified label for the actual effect. The voltage causing circulating currents is effected by phase angle errors as well as voltage differences.) The circulating current will tend to add to the load current in the transformer with the highest applied voltage. The circulating current will tend to reduce the currents in the transformers with lower applied voltages.
In your operation before failure, the two low impedance transformers would be expected to have approximately equal temperatures.
One of two similar transformers running hotter is an indication of either impending failure or of a supply voltage issue. As excess heat tends to shorten the life of a transformer, you may have been seeing a combination of unbalanced voltages and impending failure.
With a resistive load, the KVA generally equals the kW. All of the current through the load should generate heat.
A poor power factor or KVA noticeably higher than kW is an indication that not all the current is flowing through the load. That is, part of the current is circulating current.
The effect of adding a high impedance transformer will be that the available KVA will be less than the sum of the three individual transformers.
Note: The effect of increasing the voltage of the lower impedance transformer will be best at one combination of primary voltage unbalance and secondary load. Any change of primary voltage unbalance or load may result in increased circulating current.
Adding even one electrode and breaking the delta will break the circulating current.
Consider,
1> Adding one higher impedance transformer will not cause circulating currents.
2> A delta secondary is prone to circulating currents.
3> Adding a third transformer of equal impedance may not, and probably will not, eliminate the circulating currents. It may increase the circulating currents.
4> The circulating currents (kW less than KVA) are reducing the ability of the low impedance transformers to provide full kW output to the load.
5> You have two indications of circulating currents. 1: Unequal temperatures. 2: KVA much greater than kW.
Conclusion. The combination of small increase in capacity when the third transformer is added and the noticeable circulating currents may be reducing the useful capacity of the transformer bank below the capacity of two transformers running in open delta.
Suggestion. Try running in open delta with only the two low impedance transformers in the circuit. Compare the kW loading possible on open delta with the present maximum kW loading with three transformers.
Comment: The circulating currents may be a much greater issue than the mismatched impedances. In the probable event that the circulating currents are caused by voltage unbalances on the primary supply, the effect may be greater at some times than at other times. It is possible that at times, the hottest transformer was even hotter than it was when it was observed.