Miscellaneous Heat Load For Industrial machines
Miraak997
3
I have a multiple machines in a single zone, which I need to cool, I'm stuck at figuring out the percentage of heat gain from these machines out of the total electric power consumption.
I was lucky yo get the power consumption, the machines are shrink wrapping machines and sachet packaging machines.
I just want to know the average percentage to use for such machines to get the amount of the heat load.
This has been such a pain in every single industrial project, since the client wouldn't provide and documentation or data for the machines.
Typically all the work done by these type of machines is 100 percent converted to heat. However, the work done is rarely as much as the nameplate capacity of the machine. The actual work can be measured or calculated using some physics and some assumptions.
Ok. As an upper limit, about 14kW per machine. Times how many machines?
How significant is that as a percentage of your total cooling load?
They're shrink wrap machines, so as an essential part of their purpose they'll be converting a bunch of that directly into heat.
If the machine designers and original installers had any sense at all they exhausted most of that directly out the roof. Did they?
If not, you should consider doing that now. The exhaust ducts should be insulated.
Bonus points if you can recover most of that heat and use it for something useful.
You're going to need to do some data gathering to understand this properly.