When doing a network analysis, I usually keep the min V (at the peak design flow) to 0.6 m/s (2 ft/sec). This is empirical (but operational info appears to agree), to ensure that any sediment is evenly distributed (at all times) into EVERY service, rather than a few. This ensures that there is no sediment buildup (& sediment is present in almost all networks systems), with minimal dirty water complaints.
With modern subdivision layouts, some have dead end streets that do not have a ROW to connect the respective dead ends. In this case I use a 50 mm PE pipe for up to 10 services, instead of the minimum 100 mm reticulation pipe. Dead ends are always a problem due to the build up of sediment (& consumer complaints), & the same result occurs (distribution of any sediment slowly & constantly, into ALL services), rather than using flushing points at the ends of dead ends.
Fire flows are still confined to hydrants located only in 100 mm pipes, with the furthest house (from a hydrant) only 5 services distant.
If the dead end street is fairly long, a 100 mm pipe is laid until there is only 10 services left, then a 50 mm PE is used.
Since this practice was developed, the number of dirty water customer complaints (in these areas) has dropped significantly.