I'm noticing the below from ACI350-01 section 7.12.2.1 posted below. (Are excerpts allowed?)
Concrete sections that are at least 24 in. may have the minimum shrinkage and temperature reinforcement based on a 12 in. concrete layer at each face. The reinforcement in the bottom of base slabs supported
on soil may be reduced to 50 percent of that required in Table 7.12.2.1.
Suppose I have a 48" thick mat. Traditional ACI318 T&S reinforcement would be .0018*48"*12" = 1.037in2/ft.
ACI350-01 suggests that I could consider only the top 12" since the section is greater than 24" thick. I would end up with .005*12"*12"=.72in2/ft as a worst case if joints are spaced far apart.
Am I interpreting this correctly? ACI350-01 is intended for environmental engineering concrete structures so I expected more stringent requirements. This is a pretty significant difference for thicker mats.