Do ACI's minimum shear reinforcement apply to pile caps? I know it says that the minimum reinforcement requirements don't apply to "footings." Do pile caps fall under this category?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
As hokie said, compressive arching action is the structural behaviour. So as long as the compressive strut gets the column load to the piles within 45deg (roughly) and the compressive stresses limits aren't exceeded then the beam-shear requirements are not relevent.
When the strut fans out more than 45 deg is when I start introducing shear reinforcement.
However, for standard pile cap designs, I'd recommend designing to the current CRSI manual so you don't go and reinvent the wheel.
I believe that CRSI designs for shear per ACI Chapter 15 section 15.5. If pile is within d then "diagonal tension" can be neglected. It also checks for direct shear which is "real shear" for conditions where the pile is near the support.