Minimum number fo hold downs per shear wall? 1

Status
Not open for further replies.

EngineerofSteel

Structural
May 18, 2005
156
I have a two story building with a balloon frame, 22' high. The wall is attached solidly to the main building and has a height:width ratio of about 1:1.15

The tile roof anchors the wall against uplift and calculations do not require a hold down.

However, is there a minimum requirement for hold downs?

I came on to this job after the architect (who calc'd everything himself" was told he needed engineering (he does- the house is very irregular and in seismic zone 4)

This home construction permit was issued under UBC97.
 
Replies continue below

Recommended for you

'97 UBC allowed 90% of the righting moment to be used against the uplift. If there is zero or negative uplift, then no holddowns will be required.
 
I guess I need more info to believe you don't need holdowns in such a seismic zone.
 
No uplift no hold down required. However with a big heavy tile roof swaying side to side during a seismic activity it seems very likely that hold downs would be required by calculation. Verify your loads then proceed however you feel most comfortable.
 