Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Minimum cover to bottom rebar in concrete cast against void box

Status
Not open for further replies.

livewire9

Structural
Aug 4, 2010
49
ACI 318 requires concrete cover to be 3" for concrete cast against and permanently exposed to earth OR 2" for concrete exposed to earth or weather (not cast against). I believe it could be argued that a void box (used to provide separation between bottom of concrete and expansive clays) acts similar to earth. It can wick moisture. Therefore 3" cover would be prudent. Is this too conservative?
 
Replies continue below

Recommended for you

The 3" clearance takes into account the fact that soil surfaces will be highly irregular when concrete is cast against them, thus causing areas where cover is less than 3".

For cardboard void forms you will not have that degree of irregularity - thus the 2" might be a more appropriate choice.

Check out Eng-Tips Forum's Policies here:
faq731-376
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor