SacreBleu

Structural
Apr 7, 2005
427
I don't have a current ACI Code. Is there a specified minimum compressive strength for structural, reinforced, concrete walls? I would be comfortable with 28-day f'c=2500 psi for a low-rise structure, but was wondering if the ACI stated a minimum allowable.
 
Replies continue below

Recommended for you

ACI 318-02 Article 1.1.1 says: "For structural concrete, the specified compressive strength shall not be less than 2500 psi." This provision did not appear in 318-99.
 
Note that this is cross posted in the "structural engineering other topics" forum.
 