Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Minimum compressice strength for walls 1

Status
Not open for further replies.

SacreBleu

Structural
Joined
Apr 7, 2005
Messages
427
Location
US
I don't have a current ACI Code. Is there a specified minimum compressive strength for structural, reinforced, concrete walls? I would be comfortable with 28-day f'c=2500 psi for a low-rise structure, but was wondering if the ACI stated a minimum allowable.
 
ACI 318-02 Article 1.1.1 says: "For structural concrete, the specified compressive strength shall not be less than 2500 psi." This provision did not appear in 318-99.
 
Note that this is cross posted in the "structural engineering other topics" forum.
 
Status
Not open for further replies.

Part and Inventory Search