Micropiles embedded on different soils
killswitchengage
Geotechnical
Jan 5, 2015
364
Hi
Is it OK to embed micropiles on different soils knowing that they usually don't work as tip bearing fondations and that some piles are to be embedded on a weathered rock while the others on dense sands and gravel. Also there are no group effects
I would think that any soil you can safely embed them in... but you have to be well aware of potential differential settlement, and make allowance for it in the structure design and detailing.
One way to evaluate that differential settlement is to generate p-z springs for ach pile and apply them to the structural model.
You might have a difference in settlement. The geotechnical engineer can estimate the differential movement and the structural engineer would have to evaluate if the structure can handle the movement. Typically I'm using micropiles for larger structures so I tend to keep all the piles embedded into the same material.
Settlement calculations are a guess at best, especially when dealing with trying to calculate the settlement of two different soils. If your structure is sensitive to differential settlement, you may want to consider preloading the piles to "take out" any settlement effects.
That's my experience... same with concrete deflections... I was hoping that a 'bunch' of geotekkies would jump into this. I don't know what a collective of geotekkies is called? A herd, flock, cackle? Hopefully not a murder. [ponder]
Not a bad idea PEinc.
Dear structurals - pretty much all geotechnical related "calculations" are educated guesses.
That being said, if you have enough experience with load testing micropiles in the materials in question, you certainly can make an educated guess/calculation of what your differential settlement will be.
You can always design the micropiles for friction bond based in the weakest soil penetrated by the bonded length. I've never considered end bearing in my micropile designs.
killswitchengage said:
Also there are no group effects.
IMHO, for friction micropiles group effect is possible since group effect is based on the pile size / layout geometry, not soil properties.
I dont think it will be a big issue when you consider that the tip is so small compared to the shaft area and the mobilization of end bearing required to get capacity. I would guess that your differential is less than 10mm.
I have never seen a foundation that has to consider group effects. Only in very limited situations are we forced to space piles at less than 2.5-3d. Otherwise its not an issue.
Thank you all for the wonderful debate
I should point out that large scale tests were conducted using service loads.
The micro pile embedded on the rock gave high vertical capacity with minimal settlement while the one emebeded on the dense sand produced a 10 MM settlement for a 300 MM diameter pile and a lower bearing capacity, this is why I am concerned
That being said they did use vertical and horizontal springs for the overall design of these micropiles.
So the question is, can the structure tolerate approximately 10mm of differential movement? Unless it’s a bridge with separate substructures, you’ll likely have to use the same allowable load on each pile.
Sounds great... thanks.
I'd be reluctant to use rock and softer soil at the same time unless structure was detailed for it... I'm not a geotekkie, but I would try to avoid that.
