Best get your loading in place now... make sure that the purlins can support 500 lb loads at any three points and that the building frame can accommodate 2000 or 3000 lb loads at anywhere as well as 1000 lb lateral loads at any location along the vertical leg of the freame, etc. Modify above loads to suit. I'll repost my pre-eng building notes below:
METAL BUILDING SYSTEM (PRE-ENGINEERED METAL BUILDING)
DESIGN STANDARDS FOR THE METAL BUILDING SYSTEM ARE TO MEET THE REQUIREMENTS OF PART 4 OF THE MANITOBA BUILDING CODE AND CSA S16 AND CSA S136
ALL STRUCTURAL STEEL COMPONENTS, INCLUDING ANCHOR RODS SHALL BE CERTIFIED AS WELDABLE
PREFABRICATED METAL BUILDING SYSTEM SUPPLIER SHALL SUPPLY ALL ANCHOR RODS, NUTS AND WASHERS TO SECURE THE BUILDING TO THE FOUNDATION. ANCHOR RODS ARE TO BE DESIGNED FOR ALL HOR AND VERT LOADS
DESIGN OF THE BUILDING FRAME AND ALL COL MEMBERS SHALL ASSUME THAT ALL FRAME AND COL BPS ARE SUPPORTED ON 1" OF GROUT. ANCHOR RODS SHALL HAVE A MIN 3" PROJECTION ABOVE THE BP AND SHALL HAVE A MIN EMBEDMENT LENGTH AND CONFIGURATION TO RESIST ALL SHEAR AND UPLIFT FORCES
FABRICATION SHALL BE IN ACCORDANCE WITH CSA S16 AND CSA S136, AS APPLICABLE. WELDING SHALL BE PERFORMED IN ACCORDANCE WITH CSA W59 AND CSA S136. MANUFACTURER TO BE APPROVED BY THE CANADIAN WELDING BUREAU, IN ACCORDANCE WITH CSA W47.1 FOR DIVISION 1 OR DIVISION 2
THE BUILDING SHALL CARRY A 25 YEAR ROOF WARRANTY AND A 15 YEAR SIDING WARRANTY AGAINST DEFECTS IN MATERIALS AND SHALL CARRY A 5 YEAR WARRANTY AGAINST DEFECTS IN WORKMANSHIP
MIN ROOF SLOPE SHALL BE 1/2:12
THE BUILDING SHALL BE DESIGNED FOR THE FOLLOWING LOADS IN ADDITION TO THE LOADS STIPULATED IN NOTES FOR DESIGN LOADS:
ROOF PURLINS: DEAD LOAD = 5 PSF UDL
LIVE LOAD = 5 PSF UDL AND POINT LOAD OF 250 LBS SUSPENDED FROM ANY LOCATION
BUILDING FRAME: DEAD LOAD = 1000 LBS SUSPENDED FROM ANY LOCATION
LIVE LOAD = 2000 LBS SUSPENDED FROM ANY LOCATION
PURLIN BRACES ARE TO BE PROVIDED IN ACCORDANCE WITH CSA S136, CLAUSE 8. IN PARTICULAR, FOR A STANDING SEAM ROOF SUPPORTED ON MOVABLE CLIPS, BRACES PROVIDING LATERAL SUPPORT TO BOTH TOP AND BOT PURLIN FLANGE ARE TO BE PROVIDED. THE NUMBER OF ROWS SHALL BE DETERMINED BY ANALYSIS BUT IN NO CASE TO BE LESS THAN 1 FOR SPANS UP TO 23 FT. OR LESS THAN 2 FOR SPANS GREATER THAN 23 FT
ALL STRUCTURAL STEEL SHALL BE PRIME PAINTED. IF A PAINT TOP COAT IS REQUIRED, PRIMER SHALL BE COMPATIBLE WITH THE TOP COAT
ALL ROOF PURLINS AND WALL GIRTS TO HAVE A ??? COATING CONFORMING TO ???. COLOUR SHALL BE SELECTED BY THE CLIENT FROM THE MANUFACTURER'S LIST OF STANDARD PROVEN COLOURS
ALL ROOF PURLINS AND WALL GIRTS TO HAVE BE HDG WITH A COATING CONFORMING TO Z275
ALL ROOF CLADDING SHALL HAVE A COATING CONFORMING TO CSSBI [SERIES 5000 | SERIES 10000 | BARRIER | METALLIC/ELITE SERIES]. COLOUR SHALL BE SELECTED BY THE CLIENT FROM THE MANUFACTURER'S LIST OF STANDARD PROVEN COLOURS
ALL WALL CLADDING SHALL HAVE A COATING CONFORMING TO CSSBI [SERIES 5000 | SERIES 10000 | BARRIER | METALLIC/ELITE SERIES]. COLOUR SHALL BE SELECTED BY THE CLIENT FROM THE MANUFACTURER'S LIST OF STANDARD PROVEN COLOURS
ALL LINER PANELLING SHALL HAVE A ??? COATING CONFORMING TO ???. COLOUR SHALL BE SELECTED BY THE CLIENT FROM THE MANUFACTURER'S LIST OF STANDARD PROVEN COLOURS
ALL LINER PANELLING SHALL HAVE A GALVALUME COATING CONFORMING TO ZF075
COLOUR OF TRIM, RAKE, EAVESTROUGHING AND DOWNSPOUTS SHALL BE SELECTED BY THE CLIENT FROM THE MANUFACTURER'S LIST OF STANDARD PROVEN COLOURS
THE BUILDING SHALL BE INSULATED AND THE PREFABRICATED METAL BUILDING SUPPLIER SHALL SUPPLY ALL NECESSARY THERMAL BLOCKS. INSULATION SHALL BE PROVIDED BY ???
DEFLECTION OF WALL AND ROOF CLADDING SHALL BE IN ACCORDANCE WITH THE REQUIREMENTS OF CSA S136-94
DEFLECTION OF WALL GIRTS AND ROOF PURLINS SHALL BE IN ACCORDANCE WITH THE REQUIREMENTS OF CSA S16. IN ANY EVENT, LIVE LOAD DEFLECTION SHALL NOT EXCEED L/240. THE METAL BUILDING SYSTEM SUPPLIER SHALL PROVIDE FOR SUPPORT OF ANCILLARY STRUCTURAL ELEMENTS WHERE NOTED ON THE DWGS. THE METAL BUILDING SUPPLIER SHALL PROVIDE FOR REDUCED DEFLECTION LIMITATIONS AS REQUIRED FOR ATTACHMENT TO OTHER BUILDING COMPONENTS
SHOP AND ERECTION DWGS OF THE METAL BUILDING SYSTEM, BEARING THE SEAL OF A PROFESSIONAL ENGINEER REGISTERED IN MANITOBA, ARE TO BE SUBMITTED TO THE [CONSULTANT | ENGINEER] FOR REVIEW PRIOR TO THE PLACEMENT OF FOUNDATIONS. SHOP DWGS ARE TO PROVIDE LOCATION OF GRID LINES, AB CLUSTERS, AND SIZES. ANCHOR ROD AND BASE PLATE DESIGN SHALL ASSUME THAT BASE PLATES ARE SUPPORTED ON 1" GROUT
THE CONTRACTOR SHALL SUBMIT SHOP DWGS PRIOR TO FABRICATION FOR THE [CONSULTANT | ENGINEER]'S REVIEW. UNLESS NOTED OTHERWISE, SUBMIT SHOP DWGS AS FOLLOWS:
1 SET OF DWGS ON REPRODUCIBLE VELLUM
1 SET OF DWGS IN DIGITAL FORMAT
2 SETS OF PRINTS MADE FROM THE REPRODUCIBLE VELLUM
A SHOP DWG SHOWING THE ANCHOR SETTING LOCATIONS FOR THE BUILDING MUST BE PROVIDED. THIS DWG SHALL SHOW:
ANCHOR ROD LOCATIONS, TYPE, DIA, PROJECTION AND LENGTH, MAX AND MIN REACTIONS BASED ON THE LOAD COMBINATIONS STIPULATED IN THE MANITOBA BUILDING CODE SHALL BE PROVIDED FOR ALL SUPPORTS (A TABULAR FORM SHOWING LOADING REACTIONS FOR VARIOUS LOAD CASES IN NOT ACCEPTABLE)
COORD X-BRACING ELEMENTS WITH ARCH TO PREVENT CONFLICT WITH OPENINGS
THE BUILDING SHALL BE COMPLIANT WITH THE REQUIREMENTS OF ASHRAE 90.1
THE BUILDING SHALL BE COMPLIANT WITH THE REQUIREMENTS OF THE CURRENT NATIONAL ENGERGY CODE
THE BUILDING SHALL BE COMPLIANT WITH THE REQUIREMENTS OF FM GLOBAL FOR AN I-60 RATING
THE BUILDING SHALL BE COMPLIANT WITH THE REQUIREMENTS OF FM GLOBAL FOR AN I-90 RATING
THE METAL BUILDING SYSTEM MANUFACTURER SHALL SUBMIT THE CSSBI CERTIFICATE OF DESIGN AND MANUFACTURING CONFORMANCE TO THE [CONSULTANT | ENGINEER] PRIOR TO SHIPMENT OF THE PREFABRICATED BUILDING TO SITE
Bend and mutilate as necessary...
Dik