Unfortunately we are having a little bit of a disagreement in our office about something that should be simple and it is driving me nuts.
Currently, we are working on the design of a metal building foundation. The client decided that he wanted to place the bases of the column 1’-6” above the slab on grade which is causing a bit of a problem. I have attached a sketch.
Normally we would attach hairpins into the slab in order to resist the sliding forces. However, in this case the hairpins are located 1’-6” below the bottom of the footing. In my opinion, we are now getting a prying force acting on the hairpin equal to the horizontal force (H) + (the load developed in the soil to resist the force H). This is all predicated about summing the moments about A and figuring the passive pressure needed resist the horizontal load.
My colleague disagrees with this analysis. He says that you should sum forces about location B or C only because the footing will not rotate about A and therefore my analysis is incorrect. In this instance, the hairpins become virtually useless.
I know I could just not install the hairpins and size the footing appropriately, but I do not believe the client is going to be happy with the results.
How would others approach the problem?
Currently, we are working on the design of a metal building foundation. The client decided that he wanted to place the bases of the column 1’-6” above the slab on grade which is causing a bit of a problem. I have attached a sketch.
Normally we would attach hairpins into the slab in order to resist the sliding forces. However, in this case the hairpins are located 1’-6” below the bottom of the footing. In my opinion, we are now getting a prying force acting on the hairpin equal to the horizontal force (H) + (the load developed in the soil to resist the force H). This is all predicated about summing the moments about A and figuring the passive pressure needed resist the horizontal load.
My colleague disagrees with this analysis. He says that you should sum forces about location B or C only because the footing will not rotate about A and therefore my analysis is incorrect. In this instance, the hairpins become virtually useless.
I know I could just not install the hairpins and size the footing appropriately, but I do not believe the client is going to be happy with the results.
How would others approach the problem?