cctdiag, Io designates coarse adjusment ( function of In),Ir - fine adjustment - both for long time protection against overloads for electronic trip unit STR 22SE,22GE,
23SE,43 ME,53UE.The adjusment is defined as multiplication Io x Ir.
But if you have NS with termal magnetic trip unit TM-D or TM-G the adjusment of overload protection is chosen only by one pot - Ir ( rated as 0.8, 0.9 and 1 of nominal current indicated in Amps). Im in TM trip unit as for electronic indicates magnetic protection against short-circuit.
The same for motor protection trip unit STR 22ME - you have only one adjusment Ir rated in Amps for long time overload protection.
The tripping time of overload protection:
CB will trip within 2 hours for a current equal to
120% of Ir for electronic trip units
130% of Ir for thermal-magnetic
CB must not trip for a load under 105% of Ir.