X'mer ratings: 220/15.75KV // 300 MVA // OFAF // YNd1 // 10.5%
Had 220KV transformer under maintenance and vacuum pulled on tank for several days (At least 4-5). When tank under vacuum, IR at 1000 V DC was measured. Values are very good.
It is said in the manual that do not apply potential when tank under vacuum.
1) Please clarify why potential should not be applied under vacuum? What are the effects?
2) Is the megger test considered as application of potential.
Thanks,
Had 220KV transformer under maintenance and vacuum pulled on tank for several days (At least 4-5). When tank under vacuum, IR at 1000 V DC was measured. Values are very good.
It is said in the manual that do not apply potential when tank under vacuum.
1) Please clarify why potential should not be applied under vacuum? What are the effects?
2) Is the megger test considered as application of potential.