living2learn
I have a 1750kVA, 480D:12000V fuel cell step up transformer that supplies some 12kV switchgear with a main circuit breaker in a supervised location. The 480D primary is protected by a circuit breaker. The switchgear is 10' away from the transformer. I want to tap the line side of that circuit breaker and feed some new switchgear. The new switchgear feed will consist of 40' of 400A wire. This wire will tap the existing medium voltage bussing that is rated for 1200A.
When I read the NEC it mentions 240.101 (B) Feeder Taps. Conductors tapped to a feeder shall be
permitted to be protected by the feeder overcurrent device where that overcurrent device also protects the tap conductor. That tells me that the feeder OCPD must also protect the tap...the nearest OCPD is the transformer primary circuit breaker sized at 2500A.
Q1) 400A 15kV wire tapped with 100A wire must change the relays 51 settings to 100A?
Q2) I am having difficulties interprating NEC 450 becuse my transformer secondary is over 600V. I know the wire will not be damaged by the fuel cell because it cannot produce enough energy to damagage it. Therefore is my 2500A primary transformer protection enough?