Thanks for the help! In our MV application, we have control power suppliesd by external UPS panel. The reason why we're not using a CPT configuration is because we have suffered multiple sag incidents that caused MCCs to drop, losing very critical loads. But that also created an issue when technicians tripped the CB feeding this control power, when working on panel. This could've been avoided if mechanically held coils were used. We still need to make sure protection is always ON when motor is ON, so we could use a CPT circuit just for that, while keeping other control on UPS. The relay could be used to trip MCC when power is lost to satisfy requirement Bill indicated above.