Jun 21, 2021 #1 zhamal Mechanical Joined Oct 6, 2019 Messages 15 Location UZ Hi all, Should Rim vent breather valve for floating roof with mechanical shoe type sealing be installed before or after Hydrotest? All the works of Sealing are installed up to hydrotest. Tank height 21900mm, OD 37700 Product: Naphta
Hi all, Should Rim vent breather valve for floating roof with mechanical shoe type sealing be installed before or after Hydrotest? All the works of Sealing are installed up to hydrotest. Tank height 21900mm, OD 37700 Product: Naphta
Jun 21, 2021 #2 LittleInch Petroleum Joined Mar 27, 2013 Messages 22,991 Location GB either. It's not under pressure from the hydro so up to you. I would do it before. but that's just me. Remember - More details = better answers Also: If you get a response it's polite to respond to it. Upvote 0 Downvote
either. It's not under pressure from the hydro so up to you. I would do it before. but that's just me. Remember - More details = better answers Also: If you get a response it's polite to respond to it.
Jun 23, 2021 #3 IFRs Petroleum Joined Nov 22, 2002 Messages 4,682 Location US I think rim vents are vestigal and serve no purpose, so install them anytime, or not... Upvote 0 Downvote