ok fella's i am trying to get my head around this, and can't seem to grasp the concept, so i come to you with my hat in hand, hopeing to get some help.
i have a small 3 phase alternator, stator connected in Y configuration
i am measuring 80 volts phase to phase, and 18amps at load
with my clamp on meter across one leg
what i am trying to sort out is, how much power do i have in this circuit, if power factor is at unity (feeding a resistive load)?
do i calculate it as 80v x 18a =1440 watts, or do i calculate it as 3x that to account for all three legs?
or is there a 1.73 function i am missing?
i really appreciate you guys and all your help
TIA
bob g