Sdpaddler50
To the MOE experts out there; I am working on a project where a large warehouse is going to have the existing sprinklers removed, and ESFR and a pump will be added to accomodate a new tenant. There is an existing, rated exit tunnel that runs from the center of the warehouse, to an exit door on the exterior. I believe it was originally installed to meet the max 250 ft travel distanace per the original code the building was constructed to, because without this tunnel, some interior portions of the warehouse have a 275 ft travel distance to an exterior exit.
The new tenant would like to remove this tunnel, because it will interfere with their operations. If I apply the 2010 CBC and CFC, I am coming up with a 400 ft max travel distance allowed. This is based mainly on the criteria of 1016.3 of the Cal Bldg Code being met, which is below.
1016.3 Group F-1 and S-1 increase. The maximum exit access travel distance shall be 400 feet (122 m) in Group F-1 or S-1 occupancies where all of the following met:
1. The portion of the building classified as Group F-1 or S-1 is limited to one story in height,
2. The minimum height from the finished floor to the bottom of the ceiling or roof slab or deck is 24 feet (7315 mm), and
3. The building is equipped throughout with an automatic fire sprinkler system in accordance with Section 903.3.1.1.
So my question, is there any reason we would be prohibited from doing this?
IE, if the bldg is being renovated, and the MOE will satisfy the fire and bldg code criteria of the currently adopted standards by the AHJ, I belive this it is allowable to propose to the AHJ that the exit tunnel be removed.