For longer distances, a higher number of circuits are needed since the reduction in T.
c) Why SIL is one of the dominate factors? To evaluate transmission line performance, conductor rating ampacity is not enough. For example, a better indicator of a real power transferred in a radial line is P=Es.Er/X.Sin(δ). The max. power is achieved if sin(δ)=1 (δ=90o) and also if the receiving end and sending end voltages Es=Er. In this case PSIL = V2/Zc.
An example of the SIL as a useful indicator of the line performance is as follows: 1)Line loaded @ the surge impedance the voltage profile is constant along the line. 2) For load > SIL voltage is reduced at the receiving end and the opposite happens that may require shunt capacitor or reactor compensation for heavy and light load respectively.
Ze = R × PF + X L sin[arccos(PF)]
also if the receiving end and sending end voltages Es=Er
d)What are the physics behind the steady-state stability limitation? A typical T. Line operate in the real world approx.: 350 <δ< 450 limiting the power transfer to approximate to 70% to allow enough margin to withstand any sudden transient distrurbance
NOTE: • < 90o stable region. • > 90o & < 135o transient region. • > 135o unstable region.