radug
Electrical
- May 23, 2007
- 105
Hello,
When calculating the thermal rating for grounding conductors, Tm (maximum allowable temperature) must be entered in ecuation 41 of IEEE 80-2000.
The standard gives fusing temperatures of different materials (for example 1084 degrees Celsius for soft-drawn copper).
I asked some manufacturer which was the maximum allowable temperature for cadweld type welding and he told me it was above the fusing temperature for copper, so, using copper fusing temperature was ok.
My concern is, do you use some kind of conservative approach when selecting this temperature?
I have been using 250 degrees Celsius for mechanical type connections, as recommended in the standard, but I have doubts about welded connections.