A quick rule of thumb.
If the generator rated current is twice the motor rated current it may or may not start.
If the generator current is 2.5 times the motor rated current it will probably start but expect a severe voltage drop and possibly some frequency droop (which will make the voltage drop worse).
If the generator is rated at three times the motor rated current the performance is usually acceptable in all but extreme cases.
There are formulas and models, but they want the kind of input that itsmoked mentioned, and the factors he mentioned apply to these rules of thumb.
Try the major manufaturers web sites for sizing information.
Onan,
Cat,
F.G. Wilson, (Now owned by CAT)
John Deere used to publish a lot of generator data under their OEM group.
respectfully