Your english is just fine.
I agree with Metengr about the upper limit on tube velocity. Even if you don't have a silt problem, you will accelerate the wear at the vena contracta at the tube inlet with too high of a velocity.
What gage is your tube material? You might consider retubing with a thinner wall tube recognizing that you won't get the life out of it, but you will have more flow area, and can get more water through the condenser, and get a better heat rate.
In my opinion, if you are that short of surface, there is not really much you can do except to do a modular changeout of your tube bank. With a modular change out, you can change the tube diameter which allows more of a smaller diameter tube, and your tube surface ratio goes up. Plus, you can change metallurgy and if other considerations like water chemistry permit, you can choose a high heat transfer coefficient stainless or super stainless material that has high strength and can use a very thin tube wall. Modular change outs include the tubesheets, tube supports, and of course, the tubes. The support plate spacing can be decreased to accommodate the very thin wall tubes.
I have seen condenser surface areas increased up to 42% by dropping a tube size and using a 25 ga super ferritic tube.
Major condenser manufacturers offer this design.