What sushilksk said.
My utility uses the following conversion factors:
To find MW @...
500 kV: amps/1.1
230 kV: amps/2.4
115 kV: amps/4.8
44 kV: amps/13
28 kV: amps/20
14 kV: amps/41
8.3 kV: amps/120
4.8 kV: amps/208
In line with what sushilksk has indicated, these figures are based on approximations only, and are used as "rule of thumb" values; I have often found them to be meaningless when performing load transfers between different substations, i.e. when there are [too many] capacitors in service at one station but none in service at the other, and [ after parallel has been made ] the operator is attempting to derive vectorial reactive flows based on transformer secondary telemetry since the feeder breakers are only equipped with ampere telemetry, the goal being to achieve minimal reactive flow at [ by "moving the null point" to ] the intended parallel breaking point [ typically by the manually initiated raising and/or lowering of ULTCs of the supplying transformers on either side of the parallel ] prior to the actual opening of the device.
Load transfers must always be performed carefully, not only to provide minimum voltage disturbances to supplied customers but to prevent equipment damage, and even more crucially for safety reasons; if the switch being opened is being manually operated by a field agent, and is an older horn-gap air break switch with reduced arc break capabilities, and the control room operator miscalculates, molten copper may well rain down upon the head of the field agent on the switch handle below, resulting in curses being rained down upon the progeny of the control room operator - thankfully I've never had that happen to me, neither as the agent nor the controller
![[blush] [blush] [blush]](/data/assets/smilies/blush.gif)
.
Incidentally, for sixty amperes of current to flow producing one watt of real power would involve extremely low voltages; perhaps the OP meant 60A = 1 MW?
CR
"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]