Mat Foundation (1m) w/ Pedestals. Deep Beam Effects?
edomingo
AU
I have a mat foundation that supports building columns (~1m x ~1m; around edges of mat footing) and very large equipment pedestals (imagine 2mx4m pedestals; in the middle of the mat footing). The Mat Foundation is roughly 13m x 13m with Rock Anchors at the corner to help with overturning. The foundation is seated on rock so the subgrade modulus is large (~110MPa / m).
I've created a STAAD model with all the design loads on the pedestals applied to the plate mat footing and I am getting various bending (Mx,My,Mxy using Wood-Armer) in the plate bending which I am designing the reinforcement to. My question is do I have to consider "Deep Beam Effects" on footing? Or can I design the footing as a regular footing? And if this isn't the right away of designing this any advice would be appreciated!
I've designed mat foundations in STAAD in the way that you are describing. Not sure what codes you are using, but this doesn't sound like a situation where I would use deep beam provisions. My experience with models for mat foundations is that the support conditions are the driver for what results the analysis comes up with; as such it's critical your model represents closely the actual conditions. A few tips/suggestions from my experience with this are listed below:
  • Consider checking the analysis with different subgrade modulus values. I'm not a geotech but generally I think the subgrade stiffness is an input that can vary widely when it comes to actual field conditions. An upper/lower bound check could be useful
  • Make sure you are using compression only springs/plate supports for the subgrade reaction
  • Check local effects like punching shear at concentrated load locations and your rock anchors
  • Investigate the results such as bearing pressure with the program generated stress contours to verify it matches the expected behavior
  • Check vertical deflections to make sure they are within the right magnitude