sapperDAK -
The failure description (12.1.7), is only narrative.
Section 12.2 refers to information on the masonry units used to make a suggested masonry unit molded shape. That is for the engineer to determine if the mold is compatible with the units the wall is built from.
If you are using a "non-standard" mold system such as non-absorptive molds, you must fully describe (Section 12.3) the molds, sizes and proportions, correction values and coefficient of variation so the specifier can determine if it complies with the specifications that are based on the the molding method described in detail in ASTM C1019.
There is always the danger of falling into the trap of treating grout as concrete samples are treated. Concrete is placed in non-absorbent forms, while grout is placed in forms (masonry units) that absorb the excess water. Grout testing is an attempt to identify the grout in place.
All design methods, codes, specifications and testing standards are based on the tradition methods supported by years of documentation. Because of the combination of high required water contents and absorptive, it is a totally different "animal".
The grout is meant to transfer the loads from the masonry units into the steel reinforcement and are not intended to to increase the vertical compressive strength on the masonry wall. If the grout is too strong the properties of the wall are different when constructed and the load distribution is different and can lead to unpredictable failures.
If non-absorptive molds (steel, coated cardboard, etc.) of different aspect ratios, the results could require a higher strength, which is not desirable. This is the reason for the extra documentation on the mold configuration, dimensions, corrected compressive strengths and coefficient of variation, that is a source of complication and increased lab liability when the results must be compared to the methods described in C1019.
Dick